electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
- Occupation
- Electrician
Those are factory-default settings. If you're trying to coordinate with anything, let me know what the device is, and I'll send you the settings. I have access to a network package of SKM.Just a sanity check here. So on this 2000A breaker, i can turn thr long time down to .4 and use 800 A conductors yes?
Awsome thanks. Its probably not very critical in this case, its the breaker on a 400 KW generator (120/208). It will be feeding a 2000A transfer switch then a 2000A switchboard horizontal bus with 2 sections.Those are factory-default settings. If you're trying to coordinate with anything, let me know what the device is, and I'll send you the settings. I have access to a network package of SKM.
The rules for this are in 240.6(B) & (C). Most breakers fall under (C).Just a sanity check here. So on this 2000A breaker, i can turn thr long time down to .4 and use 800 A conductors yes?
Not calibrated between pointsTypically do these dials have indents at the numbers indicated and I Can only use them, or is it continuous and I can set it between two numbers?
Most of them, over the past 30 years, have pointers and detents.Typically do these dials have indents at the numbers indicated and I Can only use them, or is it continuous and I can set it between two numbers?
Ok Ill just design around those available settingsMost of them, over the past 30 years, have pointers and detents.
Setting between detents will often confuse the breaker and probably cause it assume its lowest possible settings.
If they were infinitely settable you would need to injection test the breaker to make sure it was doing what you think it should do.
Electronic relays, like an SEL, are set using software any can accept any value of pickup point.
I made good money choosing appropriate protection settings.one more question: Any advice on what I should set the other dials to? Long time will be set at about .5, maybe .6. This is the output breaker on a generator, 120/208, 400Kw. Feeding a switch board. I dont know off hand what the largest downstream OCPD is.
Those are switches, not variable resistors.Typically do these dials have indents at the numbers indicated and I Can only use them, or is it continuous and I can set it between two numbers?