Those are factory-default settings. If you're trying to coordinate with anything, let me know what the device is, and I'll send you the settings. I have access to a network package of SKM.Just a sanity check here. So on this 2000A breaker, i can turn thr long time down to .4 and use 800 A conductors yes?
Awsome thanks. Its probably not very critical in this case, its the breaker on a 400 KW generator (120/208). It will be feeding a 2000A transfer switch then a 2000A switchboard horizontal bus with 2 sections.Those are factory-default settings. If you're trying to coordinate with anything, let me know what the device is, and I'll send you the settings. I have access to a network package of SKM.
The rules for this are in 240.6(B) & (C). Most breakers fall under (C).Just a sanity check here. So on this 2000A breaker, i can turn thr long time down to .4 and use 800 A conductors yes?