electrofelon Senior Member Location Cherry Valley NY, Seattle, WA Occupation Electrician Yesterday at 11:59 PM #1 Just a sanity check here. So on this 2000A breaker, i can turn thr long time down to .4 and use 800 A conductors yes? Attachments Screenshot_20250917-205551.png 1.6 MB · Views: 2 PXL_20250917_163750491.jpg 1.1 MB · Views: 2
Just a sanity check here. So on this 2000A breaker, i can turn thr long time down to .4 and use 800 A conductors yes?
J jim dungar Moderator Staff member Location Wisconsin Occupation PE (Retired) - Power Systems 40 minutes ago #2 Yes. There is a lockable/sealable cover over the breaker setting. You meet the NEC as it does not require the settins to be inaccessible.
Yes. There is a lockable/sealable cover over the breaker setting. You meet the NEC as it does not require the settins to be inaccessible.