We have a project where there are 2 parallel sets of 500kcmil aluminum XHHW phase conductors on a circuit with 320A of operating load and a calculated load of 400A for continuous duty. These 500kcmil conductors were selected due to voltage drop. However, terminating these conductors on a 400A frame breaker or heavy duty switch is not simple. The terminals at the breaker are limited to (1) 500 or (2) 250 kcmil. The terminal limits on the disconnect are (1) 750 or (2) 300 kcmil.
Can we use a listed reducing compression splice per phase conductor that would reduce the conductor from 500 to 250 kcmil at the terminal? Then there would be only 4? of 250 kcmil conductor in the circuit. This would basically make a custom sized compression pin adapter. Code references to support your answer is appreciated.
Can we use a listed reducing compression splice per phase conductor that would reduce the conductor from 500 to 250 kcmil at the terminal? Then there would be only 4? of 250 kcmil conductor in the circuit. This would basically make a custom sized compression pin adapter. Code references to support your answer is appreciated.