Reducing conduit size going into load center panel?

Status
Not open for further replies.
Hi, as some of you may know I’m working on a project to install a meter pedestal at my land. I’ll most likely be using 500 kcmil wire and 3” conduit as the run to the build site is fairly long (300-350 ft). I’ll be using a meter / load center combo with feed through lugs. The ones I have found so far at Lowe’s have a max 2.5” or 2” knockouts. Am I allowed to reduce the 3” conduit immediately before the load center? Or do I need to find a load center with larger knockouts?
 
3" and 500 conductor is likely to large to go into that enclosure and still be compliant. I would set an in ground hand hole at the base of your pole and run 2" and smaller conductors from there to the enclosure.
 
As far as I'm aware, fittings or hardware that reduce the conduit size still affects conduit fill requirements.. even something as small as a reducing washer. Conduit fill is what you need to figure out.
 
According to the Chapter 9 C Tables... 3 x 500 kcmil THHN is still allowed in 2-1/2" EMT.

So if it's single phase (3 wires), utilizing THHN wire type, and no less than 2-1/2" EMT, you could reduce the 3" to 2-1/2" and still be code compliant.
I haven't looked at any other conduit types or wire types.
 
I missed the part about it being a pedestal. So you'll have to look at either GRC or PVC conduit fills, whatever you're using.
 
Mysteryons41, even though many of us have participated in your threads it appears as though you performing DIY work and therefor I must close your threads.

This site is designed for:

  • Electrical Contractors
  • Electricians
  • Engineers
  • Inspectors
  • Instructors
  • Other electrically related individuals
* This NEC Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.

Roger
 
Status
Not open for further replies.
Top