If you have an 800-amp breaker that can be adjusted down to 600-amp, can you use 600-amp conductors or do you need to use 800-amp? Where is this allowed in the code?
If you have an 800-amp breaker that can be adjusted down to 600-amp, can you use 600-amp conductors or do you need to use 800-amp? Where is this allowed in the code?
But there is nothing wrong with installing an 800 amp fused disconnect and using fuse reducers to install 600 amp fuses - and supply 600 amp conductors with that, or installing an 800 amp fused disconnect and installing 700 amp fuses and supplying 700 amp conductors.:blink:
Not sure if I was complaining or not. I guess the :blink: at the end sort of made it seem that way. I don't really know what to think about why the adjustable breaker has different rules then a fuseholder that can accept a variety of fuses and adapters.:roll:
Are you actually complaining the NEC is being practical?
Maybe bring up how the NEC requires a breaker to open all ungrounded conductors at once in many cases but does not require the same of fuses.
But there is nothing wrong with installing an 800 amp fused disconnect and using fuse reducers to install 600 amp fuses
I seem to recall the fuse reducers are not listed. That could be an issue.
I seem to recall the fuse reducers are not listed. That could be an issue.