sparkmatic
Member
- Location
- California
- Occupation
- Electrician/Instrumentation
I am pretty sure I know the answer to this question but want to make sure.
At the data farm we are (not my choice or design) feeding our rack pdu's from a 150A breaker with 1/0, then at the pdu it is reduced down to a #2 via a burndy splice to enter the terminal box on the pdu. 1/0 good for 150a but #2 is by NEC 115A 75C.
I can not find anything that allows this, but I do know that in the past I have seen larger conductors that are larger due to voltage drop and there is a smaller conductor splice to feed the device. The thing is the OCPD was sized say 15a and the splice conductor was rated for that amperage.
This site has terrible overloading issues and I believe this is just one of the items that need to be addressed but I don't know everything and want to make sure I am not missing something.
thanks
At the data farm we are (not my choice or design) feeding our rack pdu's from a 150A breaker with 1/0, then at the pdu it is reduced down to a #2 via a burndy splice to enter the terminal box on the pdu. 1/0 good for 150a but #2 is by NEC 115A 75C.
I can not find anything that allows this, but I do know that in the past I have seen larger conductors that are larger due to voltage drop and there is a smaller conductor splice to feed the device. The thing is the OCPD was sized say 15a and the splice conductor was rated for that amperage.
This site has terrible overloading issues and I believe this is just one of the items that need to be addressed but I don't know everything and want to make sure I am not missing something.
thanks