Here is what happened to us yesterday....
We installed a PV system (string inverter), and like we always do we used bonding bushings on all connectors and bonded all metal enclosures. This included a DC disconnect with an eccentric knockout and a PV meter socket with a concentric knockout. If it matters, the DC side is over 250V to ground and the AC side isn't.)
The inspector said that we need a 'positive bond' around the eccentric and concentric knockouts, and that the way we are supposed to do that is to sand off the paint around the knockouts and install reducing washers on the connectors. I'm not entirely sure, but I guess he is saying that we are not allowed to use the correct size knockout for our raceway but must use a larger one.
Is the inspector making any sense at all?
We installed a PV system (string inverter), and like we always do we used bonding bushings on all connectors and bonded all metal enclosures. This included a DC disconnect with an eccentric knockout and a PV meter socket with a concentric knockout. If it matters, the DC side is over 250V to ground and the AC side isn't.)
The inspector said that we need a 'positive bond' around the eccentric and concentric knockouts, and that the way we are supposed to do that is to sand off the paint around the knockouts and install reducing washers on the connectors. I'm not entirely sure, but I guess he is saying that we are not allowed to use the correct size knockout for our raceway but must use a larger one.