When starting with a 25 Amp circuit breaker then running 75 ft of #12 then branching out using # 16 awg to 4 or 6 different loads not totaling more than 25 amps with out any protection for the individual # 16 run. Is this legal according to NEC. :confused:
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Reducing Wire size with out fuse protection?

I agree with Bob.