reduction in branch circuit wiring size

Status
Not open for further replies.

cgilbert

New member
Is there a code reference that allows me to reduce my conductor size below the ampacity of my breaker at a J-box where my loads split on a terminal strip and the reduced conductors are longer than 25'?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
a few allowances for specific conditions such as 240.21 (B) 4 and 240.21 (B) for example
 

480sparky

Senior Member
Location
Iowegia
My money's on the OP wanting to reduce a 20a lighting circuit down to 14AWG for the switch loop and/or switch leg.

Oh, and welcome to the fourm!
 

wbalsam1

Senior Member
Location
Upper Jay, NY
210.19 has undergone substantial changes since the 1999 edition. For household ranges and cooking appliances, there's a tap rule that might apply. :) 210.19(A)(3) The 25' would be excessive, though.
 