Reduction of Neutral

Status
Not open for further replies.

aadams

Member
Location
Tampa, FL
Occupation
Engineer
Are you able to use the reduction factors for ranges and dryers to reduce the neutral if I used the optional calc method?
 
Yes, unless I am mis-reading 220.82
Feeder and serviceentrance conductors whose calculated load is determined by this optional calculation shall be permitted to have the neutral load determined by 220.61.
 