redundant ground in patient care areas

Status
Not open for further replies.

na112233

Member
I believe the insulated redundant ground to receps in patient care areas need to be bonded to box. Anyone agree or disagree? These are not isolated ground receps.
 
Re: redundant ground in patient care areas

Yes, they must be bonded to the box, per 250.148. Without bonding them to the box you lose the entire concept of decreased impedence in the fault clearing path.
 
Re: redundant ground in patient care areas

This would also apply to EGC's installed in metallic raceways not in patient care areas.
 
Status
Not open for further replies.
Top