T tony bryant New member Location biloxi, ms Aug 2, 2011 #1 What is the best way to test redundant grounds in a medical facility?
roger Moderator Staff member Location Fl Occupation Retired Electrician Aug 2, 2011 #2 With an Ohm meter. If you are wanting to test for equipotential you will need something a little more sophisticated such as a Fluke Bio Tek 170 analyzer or better unit and your readings must be .1 ohm or less. Roger
With an Ohm meter. If you are wanting to test for equipotential you will need something a little more sophisticated such as a Fluke Bio Tek 170 analyzer or better unit and your readings must be .1 ohm or less. Roger