Happy Friday,
I have a 120-240V sg phase three wire meter pedestal serving a common area outdoor lighting system in a residential environment. Two single pole hot conductors with one neutral and one ground wire leave the pedestal in the same conduit.
Problem: Our first electrician went out and said it was a extremely slow trip on one single pole 20A breaker. He took an amp reading on the tripped breaker after resetting it and read 10.9A. He waited two hours and it never tripped again.
I returned and read the same load and checked the other circuit, it read 8.7A. I made some repairs to some loose connections in vaults and was able to balance the outbound loads to within .5A measured on the load side of lighting contactor (9.4A and 9.6A). However, the neutral conductor reads 3A. Shouldn't the neutral in the panel read the difference between the two loads?
I have a 120-240V sg phase three wire meter pedestal serving a common area outdoor lighting system in a residential environment. Two single pole hot conductors with one neutral and one ground wire leave the pedestal in the same conduit.
Problem: Our first electrician went out and said it was a extremely slow trip on one single pole 20A breaker. He took an amp reading on the tripped breaker after resetting it and read 10.9A. He waited two hours and it never tripped again.
I returned and read the same load and checked the other circuit, it read 8.7A. I made some repairs to some loose connections in vaults and was able to balance the outbound loads to within .5A measured on the load side of lighting contactor (9.4A and 9.6A). However, the neutral conductor reads 3A. Shouldn't the neutral in the panel read the difference between the two loads?