encoreman
Member
- Location
- Austin, TX
I have new service provided by the local electric utility at a pole near the property line. There is a 120/240 VAC meter and a fused disconnect. The neutral to ground bond is established at the fused disconnect. There is underground non-metallic conduit running from the disconnect to a shelter used to house electronic equipment. The distance between the meter and the shelter is approximately 150 feet.
Because the distance between the neutral to ground bond and the shelter is greater than 75 feet (their rule) the equipment manufacturer is requiring an isolation transformer next to the building and reestablishment of the neutral to ground bond.
When I look at the code, it allows reestablishment of the neutral to ground bond only if the service was permitted under the 2005 code (or prior). Am I missing something? Is there any way to reestablish the neutral to ground bond without an isolation transformer?
Thanks!
Because the distance between the neutral to ground bond and the shelter is greater than 75 feet (their rule) the equipment manufacturer is requiring an isolation transformer next to the building and reestablishment of the neutral to ground bond.
When I look at the code, it allows reestablishment of the neutral to ground bond only if the service was permitted under the 2005 code (or prior). Am I missing something? Is there any way to reestablish the neutral to ground bond without an isolation transformer?
Thanks!