Reference Please: Conf Room Floor Outlets

Status
Not open for further replies.

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
I am working at home, and I only have the NEC 2014 and earlier. My 2017 is at my office, and my 2020 has not yet arrived. Can someone point out the rule (that I think started in 2017) concerning floor receptacles in conference rooms? I looked at the free on-line version, thinking I would find this in 210.52. But I don't see it there.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Here it is from 2017 @charlie b

210.71 Meeting Rooms.
(A) General. Each meeting room of not more than 93 m2
(1000 ft2) in other than dwelling units shall have outlets for
nonlocking-type, 125-volt, 15- or 20-ampere receptacles. The
outlets shall be installed in accordance with 210.71(B). Where
a room or space is provided with movable partition(s), each
room size shall be determined with the partition in the position
that results in the smallest size meeting room.
Informational Note No. 1: For the purposes of this section,
meeting rooms are typically designed or intended for the gathering
of seated occupants for such purposes as conferences,
deliberations, or similar purposes, where portable electronic
equipment such as computers, projectors, or similar equipment
is likely to be used.
Informational Note No. 2: Examples of rooms that are not meeting
rooms include auditoriums, schoolrooms, and coffee shops.
(B) Receptacle Outlets Required. The total number of receptacle
outlets, including floor outlets and receptacle outlets in
fixed furniture, shall not be less than as determined in (1) and
(2). These receptacle outlets shall be permitted to be located as
determined by the designer or building owner.
(1) Receptacle Outlets in Fixed Walls. Receptacle outlets shall
be installed in accordance with 210.52(A)(1) through (A)(4).
(2) Floor Receptacle Outlets. A meeting room that is at least
3.7 m (12 ft) wide and that has a floor area of at least 20 m2
(215 ft2) shall have at least one receptacle outlet located in the
floor at a distance not less than 1.8 m (6 ft) from any fixed wall
for each 20 m2 (215 ft2) or major portion of floor space.
Informational Note No. 1: See Section 314.27(B) for floor boxes
used for receptacles located in the floor.
Informational Note No. 2: See Article 518 for assembly occupancies
designed for 100 or more persons.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
A few changes in the 2020

210.65 Meeting Rooms.
210.65(A) General.
Each meeting room of not more than 93 m2 (1000 ft2) in other than dwelling units shall have outlets for nonlocking-type, 125-volt, 15- or 20-ampere receptacles. The outlets shall be installed in accordance with 210.65(B). Where a room or space is provided with movable partition(s), each room size shall be determined with the partition in the position that results in the smallest size meeting room.
Informational Note No. 1: For the purposes of this section, meeting rooms are typically designed or intended for the gathering of seated occupants for such purposes as conferences, deliberations, or similar purposes, where portable electronic equipment such as computers, projectors, or similar equipment is likely to be used.
Informational Note No. 2: Examples of rooms that are not meeting rooms include auditoriums, schoolrooms, and coffee shops.
210.65(B) Receptacle Outlets Required.
The total number of receptacle outlets, including floor outlets and receptacle outlets in fixed furniture, shall not be less than as determined in (1) and (2).
210.65(B)(1) Receptacle Outlets in Fixed Walls.
The required number of receptacle outlets shall be determined in accordance with 210.52(A)(1) through (A)(4). These receptacle outlets shall be permitted to be located as determined by the installer, designer, or building owner.
210.65(B)(2) Floor Outlets.
A meeting room with any floor dimension that is 3.7 m (12 ft) or greater in any direction and that has a floor area of at least 20 m2 (215 ft2) shall have at least one floor receptacle outlet, or at least one floor outlet to serve receptacle(s), located at a distance not less than 1.8 m (6 ft) from any fixed wall for each 20 m2 (215 ft2) or major portion of floor space.
Informational Note No. 1: See 314.27(B) for floor boxes used for receptacles located in the floor.
Informational Note No. 2: See Article 518 for assembly occupancies designed for 100 or more persons.
 