References/rules of thumb for generator stator capacitive charging current

Status
Not open for further replies.

rme291

Member
Location
Denver, CO
Occupation
Electrical Engineer
Can anyone point me to a reference that gives values/equations/rules of thumb for either the capacitive charging current or the capacitance value for a generator stator?

I am sizing a high-resistance ground resistor for a project, and I need to verify that the resistor current is greater than the system charging current, and I cannot find any references to give me these values.

Initially, we used a rule of thumb of 0.15A/1000HP, a value given in the Post Glover HRG Application Guide, but this value is for motors, not generators.

For reference, the generator information I have is:
  • 7372.5 HP (not sure where this value came from...)
  • 12,470V line-line, 7,200V line-neutral
  • Generator X/R: 29.8
 
I found the reference below, but I'm sure there are others.


This link has previews of figures and tables from the paper that give you some idea about the content of the article:

 
Status
Not open for further replies.
Top