Would like to hear from others. Its been a while since I had to do calcs for refrigeration equipment. Wanted to double check my frige and evap pan calculation. The RLA is 12.9, The MCA is 19 for the condenser unit. The evaporator pan is 5.42, and its MCA is 6.77. This is what is listed on the nameplate for equipment.
I assume they took the 12.9 X 1.25= 19, and 5.42 X 1.25= 6.77. I know the condenser unit conductors are rated at 1.25 of the amps, but is the evap unit required to be so too when it's on the same branch circuit?
And would the OCPD be the added current of the 175% (maxium) calculation of the condenser unit only? Basically, 12.9 X 1.75=22.575 + 5.42=27.99 amps. or is it both of the 125% current added, 19+6.77=25.77? I know its' a technicallity, but it's been found that the these 2 are on the same branch circuit and it's on a 20amp breaker, and it was brought up that it needed to be at least a 25amp breaker.
So far nothing has tripped.
I assume they took the 12.9 X 1.25= 19, and 5.42 X 1.25= 6.77. I know the condenser unit conductors are rated at 1.25 of the amps, but is the evap unit required to be so too when it's on the same branch circuit?
And would the OCPD be the added current of the 175% (maxium) calculation of the condenser unit only? Basically, 12.9 X 1.75=22.575 + 5.42=27.99 amps. or is it both of the 125% current added, 19+6.77=25.77? I know its' a technicallity, but it's been found that the these 2 are on the same branch circuit and it's on a 20amp breaker, and it was brought up that it needed to be at least a 25amp breaker.