Refrigerator

timmermeier

Member
Location
alton il
Occupation
electrician
Is their any code articles that say a refrigerator on a dedicated circuit ? ( any code article ) ???????????????????????????????????????????????????????
 

kwired

Electron manager
Location
NE Nebraska
No. It is permitted to be on a 15 amp individual branch circuit or on a SABC.
And that is if it is in a kitchen, dining room, pantry, etc. where SABC's are run.

A refrigerator in any other location doesn't really have any mention of of dedicated circuit unless it would happen to be large enough load to kick in rules of 210.23(B). Most typical household refrigerators don't have a load rating high enough for this to be an issue though.
 