Why is there no double pole main breaker on this panel terminating onto phase A and B feeders on top or line side of the panel according to:
408.36 switchboards, switchgear, and panel boards. Overcurrent protection. In addition to the requirements of 408.30 a panel board shall be protected by an overcurrent protective device having a rating not greater than that of the panel board. This overcurrent protective device shall be located within or at any point on the supply side of the panel board.
The branch circuit breakers do not qualify for this rule correct? Or is there possibly a breaker upstream separate from this panel?
I’ve seen panels being sold like this without such a main breaker to protect the load center
408.36 switchboards, switchgear, and panel boards. Overcurrent protection. In addition to the requirements of 408.30 a panel board shall be protected by an overcurrent protective device having a rating not greater than that of the panel board. This overcurrent protective device shall be located within or at any point on the supply side of the panel board.