Regarding the Cuicuit Breaker (MCB)
Yuyu_XX
New member
Dear all, i am really a new bee in the electrical industry, and i need to learn about the basic conponents of the cuicuit to do the design
is there anyone can kindly advice me about the MCB, especially the difference between the 1p 1p+n and 2p MCB & 3p 3p+n and 4p MCB?
as well as the usage (where & when) of the above MCBs. Thanks very much in advance
I assume 1p means a single pole breaker, 2p is a two pole breaker, and 3p is a three pole breaker.
Are you familiar with three phase systems? If not, you need to find some reading material on this.
1p+n, 2p+n and 3p+n probably means a "1 pole plus neutral", "2 pole plus neutral", and "3 pole plus neutral". That doesn't make much sense for circuit breakers because the neutral wire is never ran through a breaker, it is tied on to the neutral bus. But it does make sense for describing a load, or the wiring to the load.
The terminology you are using is not common in North America.
1P - is a single set of contacts which have overcurrent protection
1P +N - is two sets of contacts, one has overcurrent protection and the other is simply a switch. In the US we call this type of breaker a 2-wire Switched Neutral
2P - is two sets of contacts, both with overcurrent protection
3P - is three sets of contacts, all with overcurrent protection
3P + N - is four sets of contacts, three with overcurrent protection and the fourth is simply a switch
4P - is four sets of contacts, all with overcurrent protection
You can find more information by looking at literature from manufacturers that make both European and North American equipment. Try someone like Schneider Electric and their Merlin Gerin breakers.