I did a load calc for a project using a load calc program. (the one on Mike holt stuff) and it comes up with 19,220 VA. The inspector turned it down because his calcs come up with over 20,000 va
2300sq ft 2 small appliance, one laundry.....11,400
2- 2 ton a/c one with 10KW suplemental strip and on refrigerator.
The program says 19,220.
using Residential optional calculation
I have not done a manual calc in ages so i may be missing something. or is the load calc program wrong?
Thoughts
I have used the mike holt program for two years and this is first ime i have been questioned. It is a great easy program to use.
2300sq ft 2 small appliance, one laundry.....11,400
2- 2 ton a/c one with 10KW suplemental strip and on refrigerator.
The program says 19,220.
using Residential optional calculation
I have not done a manual calc in ages so i may be missing something. or is the load calc program wrong?
Thoughts
I have used the mike holt program for two years and this is first ime i have been questioned. It is a great easy program to use.