I am searching for an answer to my grounding question and this topic is fairly close to my issue. If I should create a new topic instead, please let me know!
The requirements of Chapter 5 and the confusion of RS-485 and what section governs is giving me a headache.
I am installing a Wayne dispenser for CNG fuel and I need to run RS-485 for Modbus and payment communication (card reader in display). There is also a 24VDC DI signal going to the dispenser for the methane sensor dry contacts.
We ran PVC conduit following exception No. 2 of 514.8, but I need to run an EGC. Belden 89842 (our chosen cable) does not include a ground wire, but it does include shielding.
Question: If I only have (2) RS-485 cables (Belden 89842) do I need to run a separate EGC or is one of the conductors in the cable capable of being the EGC? If not, what section governs the minimum EGC size? Table 250.122?
Question 2: If I run the 24VDC DI signal (#14s) through the same RS-485 conduit, do I just run a #14 GND?
The requirements of Chapter 5 and the confusion of RS-485 and what section governs is giving me a headache.
I am installing a Wayne dispenser for CNG fuel and I need to run RS-485 for Modbus and payment communication (card reader in display). There is also a 24VDC DI signal going to the dispenser for the methane sensor dry contacts.
We ran PVC conduit following exception No. 2 of 514.8, but I need to run an EGC. Belden 89842 (our chosen cable) does not include a ground wire, but it does include shielding.
Question: If I only have (2) RS-485 cables (Belden 89842) do I need to run a separate EGC or is one of the conductors in the cable capable of being the EGC? If not, what section governs the minimum EGC size? Table 250.122?
Question 2: If I run the 24VDC DI signal (#14s) through the same RS-485 conduit, do I just run a #14 GND?