30 HP with VFD. First trouble with it was belts slipping. Second was a broken paddle locking up the chain. Now, the third was a belt that came off leaving two, which is insufficient to handle the load. Unfortunately the slipping drive belts and locked chain result in a similar reaction. I had the current limit set to 50 amps which did shut things down with the broken paddle, but it also shuts things down as the belts slip then grab, slip/grab, making the operator think broken paddle again. Increasing the current limit to 70 amps squealed the remaining two belts, but just added to the suspicion of broken paddle. The belts are 20' feet up and require a lift to get to. Eventually the belt problem was found and stairs are now in the works for access to the belts, along with 4 belt sheaves.
Question now is 50 amp current limit or leave at 70 amp plus?