- Location
- Lockport, IL
- Occupation
- Semi-Retired Electrical Engineer
For this health care project, NEC 2008 applies. Article 700.9(B)(5)(b)'s exception allows a breaker at the backup source (diesel generator), provided that it selectively coordinates with downstream devices. Article 517 uses the term "emergency" for both the life safety and critical branches. I infer that that would bring article 700 into play. So if I have a generator that has its own breaker and that supplies life safety, critical, and equipment branches from a common board, and if the common board has separate breakers serving separate transfer switches, I believe that the breaker at the source must selectively coordinate with each of the three breakers that feed the three ATS's. Comments? Agree/disagree?