I'm looking for a rule of thumb or standard practice for setting the ground fault for a relay feeing a transformer using zero sequnce CT?
I have seen a rule of thumb for ground fault setting when using residual CT connection with the suggested pickup to be the minimum tap setting on Thr relay and the INST settikg set to 4x transformer fla at 0.2sec. The time delay of the relay is set as necessary to coordinate with other relays.
Does anyone know of any standard practice for ground pickup and INST setting with zero sequence CT's? I would think that you can set pickup to a minimum because of Zero sequence sensetivity?
I have seen a rule of thumb for ground fault setting when using residual CT connection with the suggested pickup to be the minimum tap setting on Thr relay and the INST settikg set to 4x transformer fla at 0.2sec. The time delay of the relay is set as necessary to coordinate with other relays.
Does anyone know of any standard practice for ground pickup and INST setting with zero sequence CT's? I would think that you can set pickup to a minimum because of Zero sequence sensetivity?