Can lighting control panel take both 120V and 277V lighting circuits?
300.3.C(1) may allows? Thank you.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes also take a look at 200.6(D) which would apply when you had 120 and 277 volt circuits.
 

anbm

Senior Member
Location
TX
Occupation
Designer
Yes also take a look at 200.6(D) which would apply when you had 120 and 277 volt circuits.

What're about 404.1 and 404.8(B) rules? Will barrier still required between 120V and 277V circuit relays even they are less than 300V?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
404.8(B) is for adjacent snap switches. A relay is not a snap switch so no barrier is required.
 