C chop New member Nov 8, 2010 #1 Fellow worker asked, "if I had ever found any thing in the nec. about not being able to mount ice cube relays inside back box of panel to control lighting". Anyone come across this? thanks
Fellow worker asked, "if I had ever found any thing in the nec. about not being able to mount ice cube relays inside back box of panel to control lighting". Anyone come across this? thanks
ron Senior Member Location New York, 40.7514,-73.9925 Nov 8, 2010 #2 It would be a listing issue, and/or a gutter space issue [NEC 408.55].
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Nov 8, 2010 #3 Depending on the purpose for the relay and the type cables supplying it, you might enounter an Art 725 issue.
Depending on the purpose for the relay and the type cables supplying it, you might enounter an Art 725 issue.