Hi All,
I work in an office building that has each floor
powered by a 45 kVA 440V delta / 208 wye
transformer with our office using 120 V phase to
neutral connections. For the past day I have
been monitoring a line voltage continuously
by setting an oscilloscope on infinite
persistence. During this time a bit over
a million acquisitions were made and superimposed
over each other. The RMS voltage has ranged from
115.8 V to 149.9 V. I have previously noticed
voltages around 130 V using a voltmeter, and I
have asked the building supervisor to correct
this a couple of times. To date nothing has
been done, so I would like to know what this
violates.
Also, I have measured over 3 V from neutral to
ground which seems quite high. Assuming equal
voltage drop on each wire, this would be a total
of about 7 V voltage drop in the circuit (about
6%), and that was not even with much known load
applied. Is this allowable? Incidentally, this
is a fairly new building. Thanks for any
information.
Jim Monte
I work in an office building that has each floor
powered by a 45 kVA 440V delta / 208 wye
transformer with our office using 120 V phase to
neutral connections. For the past day I have
been monitoring a line voltage continuously
by setting an oscilloscope on infinite
persistence. During this time a bit over
a million acquisitions were made and superimposed
over each other. The RMS voltage has ranged from
115.8 V to 149.9 V. I have previously noticed
voltages around 130 V using a voltmeter, and I
have asked the building supervisor to correct
this a couple of times. To date nothing has
been done, so I would like to know what this
violates.
Also, I have measured over 3 V from neutral to
ground which seems quite high. Assuming equal
voltage drop on each wire, this would be a total
of about 7 V voltage drop in the circuit (about
6%), and that was not even with much known load
applied. Is this allowable? Incidentally, this
is a fairly new building. Thanks for any
information.