I’m working on adding an automatic transfer switch between my meter and my house panel. From what I understand I need to isolate the grounds and neutrals as the house panel will now be a sub panel. Is it ok to just run a ground wire from the ATS to the ground bus bar on the house panel or do I need to relocate the electrode ground and the gas and water bonds to the ATS? If I need to relocate the electrode, gas, and water bonds, can I extend them some how as they are not long enough to get out to the transfer switch.
Thanks for your help.