Here's the scenario:
Older house/apt, (1940's 50's) wired with older NM cable 12/2, no grounding conductors.
Relocating a receptacle, which is a feed-through, with a need to add a piece of new 12/2 NM to go from the relocated to the next receptacle in line. (And it will be pigtailed, not using the device for the feed thru.)
The new 12/2 NM obviously has a ground conductor, which in this case doesn't return all the way to the panel, but simply runs from one box to the other.
Do you:
1) Leave the grounding conductor in place in each box, but tucked back out of the way;
2) Connect it to the devices at each end (and bond to the boxes if metal);
3) Cut the grounding conductor off at each end, at the end of the sheath so it cannot be used;
OR- and here's a kicker:
4) Connect a single 12 THHN green wire and tap into the grounding conductor of a nearby box, even though it is on a different circuit? (Distance would be about 6 feet.)
I kinda feel options 3 or 4 would be best, depending on if Code would allow either.
Let's hear what you all think!!
Do you: