The simple answer is that it can't be done because the Code says it can't.Originally posted by acn24:
This project is in a 1 bedroom apartment( 1 occupant ). Is it not allowed due to access or is it because it is in a damp location ?
Impromtu piggybank? Industrial grade cereal bowl?Now, what are you going to do with an empty panelboard?
Tony I believe you can replace the panel and leave it in the bathroom. Your application is not affected by 240.24E. You have my blessings although you may want to avoid a fight with the inspector and let him/her know what you are going to do.TonyEEINC said:I have read the threads about this ?
I have a Sub panel, that is currently in the bath of a Eye DR. office. We are going to remove it because it is a Fed. Pac.
The Dr. wants it back in the same place.
Searching the NEC I read 230.70.A.2 that states Service disconnects shall not be in Bathrooms.
My service disconnect is outside.
then 240.24.E states
Overcurrent devices in dwellings, hotel, motel guest suites, shall not be in bathrooms.
This still does not cover my Sub panel.
I think I can leave it as the Dr. wants.
I do however have a call in to the A. H. J.
So we will see.
Tony
amptech said:I think panels in bathrooms are only prohibited in dwellings. Otherwise every Walmart in America would be in violation of the NEC.