Greetings,
I have a single-family dwelling supplied by primary service and a standby generator with a 200-amp transfer switch: I am upgrading the 120V breakers in a 200-amp main lug CB panel (surface mount inside wall). It is supplied by 200-amp outside meter/load panel (one 200-amp breaker disconnect) and the standby generator transfer switch if the primary service fails. The transfer switch does not provide any load center capability for circuit breakers.
I am upgrading the 120V breakers in the inside panel to AFCI/GFCI breakers. There is an EATON CHSPT2ULTRA installed at the breaker panel. The breaker connected to the SPD is a Siemens tandem 15/5050/15 breaker. I have to split the circuit into two 15-amp dual function breakers for AFCI/GFCI protection. There is not enough room in the cabinet for a double-pole 50-amp breaker and separate 15amp breakers. I have not been able to find the new Siemens Tandem Combination AFCI breakers that I could use to make space for the 50-amp double pole breaker.
I have decided to relocate the Type 2 SPD to the outside 200-amp meter/load center and install a 50-amp breaker in the panel and attach the SPD to the outside of the panel trough a 1/2" conduit knockout.
I cannot find anything in the 2020 NEC that details SPD protection when a Type 2 SPD is on the load side of the meter/load panel and a transfer switch is between the meter/load center and the main inside panel. The SPD should be on the load side of both sources of power but I don't have that solution. Does anyone have a suggestion on how to provide surge protection when the generator is powered on and supplying power to the inside panel? Does it require an adjacent subpanel, powered by the main, inside, CB panel, with breakers for the Type 2 SPD and the two 15-amp circuits?
One more question, please: If the Type 2 SPD is connected to an outside panel, does it need GFCI protection?
I have a single-family dwelling supplied by primary service and a standby generator with a 200-amp transfer switch: I am upgrading the 120V breakers in a 200-amp main lug CB panel (surface mount inside wall). It is supplied by 200-amp outside meter/load panel (one 200-amp breaker disconnect) and the standby generator transfer switch if the primary service fails. The transfer switch does not provide any load center capability for circuit breakers.
I am upgrading the 120V breakers in the inside panel to AFCI/GFCI breakers. There is an EATON CHSPT2ULTRA installed at the breaker panel. The breaker connected to the SPD is a Siemens tandem 15/5050/15 breaker. I have to split the circuit into two 15-amp dual function breakers for AFCI/GFCI protection. There is not enough room in the cabinet for a double-pole 50-amp breaker and separate 15amp breakers. I have not been able to find the new Siemens Tandem Combination AFCI breakers that I could use to make space for the 50-amp double pole breaker.
I have decided to relocate the Type 2 SPD to the outside 200-amp meter/load center and install a 50-amp breaker in the panel and attach the SPD to the outside of the panel trough a 1/2" conduit knockout.
I cannot find anything in the 2020 NEC that details SPD protection when a Type 2 SPD is on the load side of the meter/load panel and a transfer switch is between the meter/load center and the main inside panel. The SPD should be on the load side of both sources of power but I don't have that solution. Does anyone have a suggestion on how to provide surge protection when the generator is powered on and supplying power to the inside panel? Does it require an adjacent subpanel, powered by the main, inside, CB panel, with breakers for the Type 2 SPD and the two 15-amp circuits?
One more question, please: If the Type 2 SPD is connected to an outside panel, does it need GFCI protection?