So I am installing a switchgear and I see a small dial on the gear labeled main relt switch I asked my foreman what it was and he had no idea what's the main relt switch for
What's dose that switch do ?Reduced Energy Let Through.
Can you please elaborate I'm not understandingCould be shorthand for Reduced Energy Let Through... basically an override to your usual breaker trip settings in order to knock down the arc flash energy during maintenance.
I'm guessing this reduces the arc flash on the load side of the main switch gear not the line side ??
CorrectI'm guessing this reduces the arc flash on the load side of the main switch gear not the line side ??
I know nothing about them; I'm just good at finding stuff.I'm guessing this reduces the arc flash on the load side of the main switch gear not the line side ??
Arc Flash has nothing to do with series or parallel arcs. Those term are associated with Arc-Fault.I would guess they reduce fault current everywhere, so they would reduce series arcing everywhere, but parallel arcing only downstream.
If there is a phses to phase short on the load side of the main i see how the relt will reduce the arc but how would it help on the line side ?Arc Flash has nothing to do with series or parallel arcs. Those term are associated with Arc-Fault.
Arc Flash is what sends 'electricians' to the hospital, it is why PPE is needed.
The RELT causes the circuit breaker to react to the fault faster with the hope that it clears the arc sooner.If there is a phses to phase short on the load side of the main i see how the relt will reduce the arc but how would it help on the line side ?
A RELT is used when working on downstream, physically separated gear.It is used whenever you work on the gear,
It does nothing for the line side, but it is for anything on the load side.A RELT is used when working on downstream, physically separated gear.
It does nothing for the gear in which it is installed. Thus is a common misunderstanding with main devices in multisection switchboards.
My suggestion was always for Main devices to be in standalone sections with cable and conduit feeds to distribution sections. But people don't like the cost and the extra real estate.
Has any manufacturer developed a switchboard barrier that they advertise as stopping arcs?
Not for direct connected equipment.It does nothing for the line side, but it is for anything on the load side.