i have a 400A 480v panel that i am running some machinery off of. currently i have a total of 168,482VA total from the nameplates, 64,000 VA is the biggest load.
max demand = 168.482x1.25=210,602.5
210,602/(1.732×480)=253.3A
253.3x1.25=316.6A
400A-316.6=83.4A ampacity remaining
83.4/1.25=66.72A demmand remaining
66.72/1.25=53.376A rated remaining
does this look right? i can still put about 54A of load on my panel? let me know your thoughts and what area of code I should look at, thanks for the help
max demand = 168.482x1.25=210,602.5
210,602/(1.732×480)=253.3A
253.3x1.25=316.6A
400A-316.6=83.4A ampacity remaining
83.4/1.25=66.72A demmand remaining
66.72/1.25=53.376A rated remaining
does this look right? i can still put about 54A of load on my panel? let me know your thoughts and what area of code I should look at, thanks for the help