When using the white wire in MC or romex as an ungrounded conductor are we allowed to use it as a travelor in a 3 way circuit ? I think we covered this once but i need a code referance
That is pretty clever, did you post that in, I belive its ECM or one of those electrical magazines, you may win a neat prize, as for using the white for ungrounded conductor as long as its marked.What I found is the easiest way to remark up to a #4 (have had no neeed to remark any larger) us to drop in at Walmart.Go to office/school supply and look for one of those big a_ _ grafitti markers,cut a V into the long side and when you need to remark an ungrounded conductor or in as your case part of a 3 wire cable assy.A couple of swipes and done deal.
I personally liked r & b, but have seen old timers also use r & w
Originally posted by wildman:
attended a continuous education class a few weeks ago. instructor got in a hurry up mode toward the end and I am not sure about two items;
1. 2005 nec code says wires can only be remarked if larger than #6 AWG
Nope, this text hasn't changed from the 2002.
2. 2005 nec code says the entire circuit of a GFCI circuit must be protected....can no longer run(example) 50 feet of romex to the first receptacle (gfci)....
Exception: install a gfci receptacle within 5 feet of breaker panel, then its ok!
Nope, that's AFCI protection, not GFCI. But no worries, it's a post-dated check: The existing method will be acceptable until 2008.
[/b]
No, when we re-color a white, we're declaring it to no longer be a neutral. There's no rule that any color must be "always hot", whether factory or re-colored.Originally posted by rasmithircgov.com:
The white as Traveler isnt always going to be hot. One time it will and one time it wont. Depending on position of switch. So your telling me that your going to mark a wire as hot that isnt going to be hot continuiosly. We mark white as hot at the breaker when used. It's continuosly hot. I believe its not to code to mark a switch leg or travelers as hot when it wont be continuosly hot.
What 200.7(C)(2) says (at least in my opinion) is that you can use the re-identified conductor as a traveler, but not as the switched leg to the switched outlet. What you're missing is the part where it says, "...return conductor from the switch to the switched outlet ". That's the key to what you can do with the re-identified white conductor.Am I lost here or does this Art. say" supply to the switch but not as a return conductor from the switch.... Is that not the travelers. What is it Im missing?