Good day everyone. Service Calc question.
Working the electrical design for the remodel of a multi-story apartment (1960 original build) (not a high rise). 150 existing resident rooms (dwelling units) (range/cook top and existing dedicated electrical panel to the room).
Dwelling Unit Rooms:
Central boiler system for heating. Baseboard hot water in each DU.
Central Laundry
Central hot water
Original design of the building did not include cooling for the resident rooms. At some point (not sure the year) they allowed the residents to utilize thru wall / window, 120v residential plug in AC units. (Staff removes them each Fall and reinstalls each spring) (about 75 of the residents utilize them... so half). The resident supplies them, so they are all different. Nameplate was 6.5a - 120v on one I noted.
Project Scope - or the DU rooms: paint up, carpet, new casework, 1 for 1 electrical device replacement, resident room electrical panel replacement, FA upgrade, and permanent cooling (condensing unit mounted on the exterior wall outside the room - 1 for each room) w/ high wall fan inside. 208v/1P - 15 FLA (fan powered via outdoor unit). Stated as a Level 1 remodel.
Existing electrical building service is a 1600 amp 208/120v 3P service. Peak load was 180 KW - highest in the last 24 months.
Question:
I need to verify the existing 1600-amp service is not overloaded.
I believe I should apply - NEC 220.83(b). I arrive at 37 amps at 208v / 3P per this calc. for each resident room.
I believe I then can apply Table 220.84 Optional Calc - Demand Factor. 62 Dwelling units and over is a Demand Factor of 23 percent. 37a per room x 150 rooms x 23 percent equals 1277 amps, without House loads. Per this direction the 1600 is overloaded... if I applied everything correctly?
Code possible to attack the service calc. in another manner, since we have the 24-month peak load? Possible to apply the new AC DU loads (15a at 208v/1P) in each room (150) x the 23 percent in Table 220.84 plus peak load at 125 percent? Options?
Your input is appreciated. Thank you.
Working the electrical design for the remodel of a multi-story apartment (1960 original build) (not a high rise). 150 existing resident rooms (dwelling units) (range/cook top and existing dedicated electrical panel to the room).
Dwelling Unit Rooms:
Central boiler system for heating. Baseboard hot water in each DU.
Central Laundry
Central hot water
Original design of the building did not include cooling for the resident rooms. At some point (not sure the year) they allowed the residents to utilize thru wall / window, 120v residential plug in AC units. (Staff removes them each Fall and reinstalls each spring) (about 75 of the residents utilize them... so half). The resident supplies them, so they are all different. Nameplate was 6.5a - 120v on one I noted.
Project Scope - or the DU rooms: paint up, carpet, new casework, 1 for 1 electrical device replacement, resident room electrical panel replacement, FA upgrade, and permanent cooling (condensing unit mounted on the exterior wall outside the room - 1 for each room) w/ high wall fan inside. 208v/1P - 15 FLA (fan powered via outdoor unit). Stated as a Level 1 remodel.
Existing electrical building service is a 1600 amp 208/120v 3P service. Peak load was 180 KW - highest in the last 24 months.
Question:
I need to verify the existing 1600-amp service is not overloaded.
I believe I should apply - NEC 220.83(b). I arrive at 37 amps at 208v / 3P per this calc. for each resident room.
I believe I then can apply Table 220.84 Optional Calc - Demand Factor. 62 Dwelling units and over is a Demand Factor of 23 percent. 37a per room x 150 rooms x 23 percent equals 1277 amps, without House loads. Per this direction the 1600 is overloaded... if I applied everything correctly?
Code possible to attack the service calc. in another manner, since we have the 24-month peak load? Possible to apply the new AC DU loads (15a at 208v/1P) in each room (150) x the 23 percent in Table 220.84 plus peak load at 125 percent? Options?
Your input is appreciated. Thank you.