I'm in the process of specifying a field enclosure which will contain a remote I/O subsystem located in a C1D2 rated area. There are 4 main components in the field enclosure: module power supply, communications module, remote I/O modules and a second 24 VDC power supply for the instrument loops. All 4 of these components are specified by the manufacturer as being rated for Class 1 Division 2. A NEMA 4 enclosure will be specified.
I will be connecting 120 VAC to both 24 VDC power supplies. An ethernet cable will be connected to the communications adapter.
The field instrumentation is all specified as non-incendive, rated for Class 1 Division 2. Hence, no IS barriers are needed.
Given that all of the interior panel components and instrument interfaces meet C1D2, per Articles 501/504, it is my understanding that I do not need to Z-Purge this panel or do anything beyond installing the components. It is also my understanding that I'll need to wire the 120 VAC to the power supplies in a manner to avoid the potential for an arc.
Does all of this sound feasible, or am I overlooking something here? Be kind, this is my first post in this forum - Thanks.
I will be connecting 120 VAC to both 24 VDC power supplies. An ethernet cable will be connected to the communications adapter.
The field instrumentation is all specified as non-incendive, rated for Class 1 Division 2. Hence, no IS barriers are needed.
Given that all of the interior panel components and instrument interfaces meet C1D2, per Articles 501/504, it is my understanding that I do not need to Z-Purge this panel or do anything beyond installing the components. It is also my understanding that I'll need to wire the 120 VAC to the power supplies in a manner to avoid the potential for an arc.
Does all of this sound feasible, or am I overlooking something here? Be kind, this is my first post in this forum - Thanks.