A aarifisher Member Feb 26, 2010 #1 Which article covers the disconnect rules for a building that its service is located on a pole about 20ft off of the building.
Which article covers the disconnect rules for a building that its service is located on a pole about 20ft off of the building.
raider1 Senior Member Staff member Location Logan, Utah Feb 26, 2010 #2 Article 225. Specifically section 225.31 Chris
A aarifisher Member Feb 26, 2010 #3 So if this service on the pole is only serving one building would you consider this under part 2 of article 225
So if this service on the pole is only serving one building would you consider this under part 2 of article 225
raider1 Senior Member Staff member Location Logan, Utah Feb 26, 2010 #4 aarifisher said: So if this service on the pole is only serving one building would you consider this under part 2 of article 225 Click to expand... Yes, the pole itself is a structure. Therefore you have the service mounted on a structure that is in turn feeding a second building. See the definition of structure from Article 100. Structure. That which is built or constructed. Click to expand... Chris
aarifisher said: So if this service on the pole is only serving one building would you consider this under part 2 of article 225 Click to expand... Yes, the pole itself is a structure. Therefore you have the service mounted on a structure that is in turn feeding a second building. See the definition of structure from Article 100. Structure. That which is built or constructed. Click to expand... Chris