I am a new member here so I hope this is the correct forum. I live out in Ma (lic journeyman). I recently received a call from a customer who says the water dept. has informed him he must remove his grounding electrode conductor (GEC) from their incoming water pipe. I asked if it was because they were running a new pipe, replacing the old pipe or changing the incoming pipe to PVC. However I was told it is simply because they believe that using the incoming water pipe as the grounding electrode (GE) is causing the water pipe to corrode and pit, creating leaks between the meter and out in the street. Has anyone ever heard of this b-4??
I certainly have no problem driving a supplemental ground rod/rods. However even if I did so my interpretation of 250.52 (A)1 is that if I have a metallic water pipe in contact with 10 feet of earth it is a GE and if present all defined GE's shall bonded together to form a single GE system. So would I not required to at least put a wire (bonding) right back(including a meter jumper) where they are saying to take the GEC off?? It sounds like they are doing this all over town. My concern is that if I knowingly violate the code I would be liable for any problem that might ensue.Any help would be appreciated
Thanks
I am a new member here so I hope this is the correct forum. I live out in Ma (lic journeyman). I recently received a call from a customer who says the water dept. has informed him he must remove his grounding electrode conductor (GEC) from their incoming water pipe. I asked if it was because they were running a new pipe, replacing the old pipe or changing the incoming pipe to PVC. However I was told it is simply because they believe that using the incoming water pipe as the grounding electrode (GE) is causing the water pipe to corrode and pit, creating leaks between the meter and out in the street. Has anyone ever heard of this b-4??
I certainly have no problem driving a supplemental ground rod/rods. However even if I did so my interpretation of 250.52 (A)1 is that if I have a metallic water pipe in contact with 10 feet of earth it is a GE and if present all defined GE's shall bonded together to form a single GE system. So would I not required to at least put a wire (bonding) right back(including a meter jumper) where they are saying to take the GEC off?? It sounds like they are doing this all over town. My concern is that if I knowingly violate the code I would be liable for any problem that might ensue.Any help would be appreciated
Thanks