Morning, can somebody please explain the reasoning behind REMOVING THE GROUND FROM THE NEUTRAL OF AN EXISTING SERVICE ENTRANCE EQUIPMENT, AND GROUND TO NEUTRAL ON THE NEW SERVICE ENTRANCE EQUIPMENT?

Thanks!
 
Morning, can somebody please explain the reasoning behind REMOVING THE GROUND FROM THE NEUTRAL OF AN EXISTING SERVICE ENTRANCE EQUIPMENT, AND GROUND TO NEUTRAL ON THE NEW SERVICE ENTRANCE EQUIPMENT?

Thanks!
Is the new service entrance equipment being installed on the line side of the existing service entrance equipment?
 
"Is the new service entrance equipment being installed on the line side of the existing service entrance equipment?"



Yes that is correct, it is now the new service entrance equipment.

Thanks
 
"Is the new service entrance equipment being installed on the line side of the existing service entrance equipment?"



Yes that is correct, it is now the new service entrance equipment.

Thanks
The connection between the grounded conductor and the grounding system cannot be on the load side of the service disconnect, so you will have to move it to the new service disconnect. See 250.24(A)(5). You will have to separate the grounding conductors from the grounded conductor at the old service equipment and you will have to install a feeder between the new and old equipment that includes an EGC.
 
"Is the new service entrance equipment being installed on the line side of the existing service entrance equipment?"



Yes that is correct, it is now the new service entrance equipment.

Thanks

That would mean that the new service entrance equipment would be the primary point of disconnect for the system if I understand your question. If that's the case the GEC should be connected there and the neutral bonded (with the supplied green bonding screw) to the panel. The original service now becomes a sub panel and cannot be bonded as this would potentially cause objectionable currents in the ground system. I hope that helps.
 
The connection between the grounded conductor and the grounding system cannot be on the load side of the service disconnect, so you will have to move it to the new service disconnect. See 250.24(A)(5). You will have to separate the grounding conductors from the grounded conductor at the old service equipment and you will have to install a feeder between the new and old equipment that includes an EGC.


That explains it, thank you so much"
 
If this service equipment is fed from a xfmr( customer owned) as in a 480v -xfm- 208. The grounded and grounding conductors may be bonded there. Then they would be separated at the service equipment.
 
If this service equipment is fed from a xfmr( customer owned) as in a 480v -xfm- 208. The grounded and grounding conductors may be bonded there. Then they would be separated at the service equipment.

That is an impossible scnerio.

If there is a customer opened 480 x 208/120 transformer the service equipment would have to be located on the line side of it.
 
Mr.iwire what is it that I'm understanding in correctly?
That the secondary isn't called or considered service equipment.
If the transformer is customer owned, the secondary conductors are feeder conductors and not service conductors. Service conductors can only be
supplied by a direct connection to the serving utility. Any other source supplies feeders or branch circuits.
 