Is the new service entrance equipment being installed on the line side of the existing service entrance equipment?Morning, can somebody please explain the reasoning behind REMOVING THE GROUND FROM THE NEUTRAL OF AN EXISTING SERVICE ENTRANCE EQUIPMENT, AND GROUND TO NEUTRAL ON THE NEW SERVICE ENTRANCE EQUIPMENT?
Thanks!
The connection between the grounded conductor and the grounding system cannot be on the load side of the service disconnect, so you will have to move it to the new service disconnect. See 250.24(A)(5). You will have to separate the grounding conductors from the grounded conductor at the old service equipment and you will have to install a feeder between the new and old equipment that includes an EGC."Is the new service entrance equipment being installed on the line side of the existing service entrance equipment?"
Yes that is correct, it is now the new service entrance equipment.
Thanks
"Is the new service entrance equipment being installed on the line side of the existing service entrance equipment?"
Yes that is correct, it is now the new service entrance equipment.
Thanks
The connection between the grounded conductor and the grounding system cannot be on the load side of the service disconnect, so you will have to move it to the new service disconnect. See 250.24(A)(5). You will have to separate the grounding conductors from the grounded conductor at the old service equipment and you will have to install a feeder between the new and old equipment that includes an EGC.
If this service equipment is fed from a xfmr( customer owned) as in a 480v -xfm- 208. The grounded and grounding conductors may be bonded there. Then they would be separated at the service equipment.
If the transformer is customer owned, the secondary conductors are feeder conductors and not service conductors. Service conductors can only beMr.iwire what is it that I'm understanding in correctly?
That the secondary isn't called or considered service equipment.