Just want to check that I understand this....

I have a repair garage and the floor up to 18" is a hazardous area. Everything above the 18" can be installed a non hazardous instllation?

If I avoid the 18" zone with my receptacles and other equipment I am fine...?
 
As long as everything is fed from overhead and not coming out of floor (seal offs would be needed). Also, all receptacles (120 Volt) must be GFCI protected.
 
Hoyt said:
Just want to check that I understand this....

I have a repair garage and the floor up to 18" is a hazardous area. Everything above the 18" can be installed a non hazardous instllation?

If I avoid the 18" zone with my receptacles and other equipment I am fine...?

its not as simple as that, you might want to read article 511. 511.3 explains very clearly what areas are to be classified.
 