Ok, the code talks about repair garages in 511. The areas next to the service bay, in this case a showroom, what is an effective wall as stated:
511.A(3) Specific Areas Adjacent to Classified Locations - Areas adjacent to classified locations in which flammable vapors are not likely to be released, such as stock rooms, switchboard rooms, and other similar locations, shall not be classified where mechanically ventilated at a rate of four or more air changes per hour, or designed with positive air pressure, or where effectively cut off by walls or partitions.
Can this be a sheet rock wall, or will concrete be required?
The handbook has a picture (I know, not code!) that shows the door's sill to be not less then 18" above the hazardous location's floor. I can not find any wording in the code to support this. NFPA 30A either. The ICC 2000 IBC has wording that the wall must not have openings except for fire rated, self closing doors.
Writting contradictions.
511.A(3) Specific Areas Adjacent to Classified Locations - Areas adjacent to classified locations in which flammable vapors are not likely to be released, such as stock rooms, switchboard rooms, and other similar locations, shall not be classified where mechanically ventilated at a rate of four or more air changes per hour, or designed with positive air pressure, or where effectively cut off by walls or partitions.
Can this be a sheet rock wall, or will concrete be required?
The handbook has a picture (I know, not code!) that shows the door's sill to be not less then 18" above the hazardous location's floor. I can not find any wording in the code to support this. NFPA 30A either. The ICC 2000 IBC has wording that the wall must not have openings except for fire rated, self closing doors.
Writting contradictions.