The breaker is mechanically interacting with the bus and a mechanical fault while racking the breaker in or out can result in a electrical fault and an arc flash.If the circuit breaker is off, manually cranking it out to replace it doesn't seem like an arc fault hazard. Please elaborate.
One of the simplest possibilities is a mechanical failure that breaks either the bus or the CB jaws loose. Think of pulling out a meter from its socket and finding yourself holding a meter with one wire still attached.If the circuit breaker is off, manually cranking it out to replace it doesn't seem like an arc fault hazard. Please elaborate.
Racking a breaker onto or off of live bus is usually considered to be a very high risk for creating an arc fault event. Most manufacturers offer remote racking provisions because of this risk.If the circuit breaker is off, manually cranking it out to replace it doesn't seem like an arc fault hazard. Please elaborate.
Fortunately, you never had to do it.Thanks for the replies. When I was an apprentice I was working with a j-man who was manually racking out a breaker. He promised he would teach me how to do it, but it never happened. I've always felt like that was a hole in my training.
Well I've had the opportunity to consider bidding on some local gov't work where we would be doing maintenance of switchgear or doing on-call work. As I said, I don't feel competent to rack out a breaker, but I can hire industrial electricians who are. I figured if I happened to win one of these, I could have my employee teach me how to do it.Fortunately, you never had to do it.
The alternative is a full-on bunny suit. But with high enough arc energy the mechanical forces and shrapnel could still kill you.
And there is a lot of industrial swithgear where the incident energy from a fault at the bus exceeds 40 cal. Often these are marked with a label prohibiting local operation while the equipment is energized. That includes both on and off operations as well as racking operations. Typically facilities with this marking have remote operation and racking equipment available on site.Well I've had the opportunity to consider bidding on some local gov't work where we would be doing maintenance of switchgear or doing on-call work. As I said, I don't feel competent to rack out a breaker, but I can hire industrial electricians who are. I figured if I happened to win one of these, I could have my employee teach me how to do it.
Based on what you guys have said, and assuming they don't have remote racking, now I'm thinking that this would be a big workman's comp liability issue and at minimum I would have to provide a high cal arc flash suit which I assume is expensive. I probably won't be bidding these kind of jobs, but now I feel like I'll never have a chance to learn this skill.
if there is a "high risk" of an arc fault, I think I would not be engaging in that activity even if I had a blast suit on and the IE was fairly low.Racking a breaker onto or off of live bus is usually considered to be a very high risk for creating an arc fault event. Most manufacturers offer remote racking provisions because of this risk.
I agree.if there is a "high risk" of an arc fault, I think I would not be engaging in that activity even if I had a blast suit on and the IE was fairly low.