replace existing recpt arc fault tamperproof 2011 code ?

Status
Not open for further replies.
replacing recpt. in existing dewelling do they need be arc fault as well as tamper proof for the 2011 code

406.4
(4) Arc-Fault Circuit-Interrupter Protection. Where a receptacle outlet is supplied by a branch circuit that requires arc-fault circuit interrupter protection as specified elsewhere in this Code, a replacement receptacle at this outlet shall be one of the following:




  1. A listed outlet branch circuit type arc-fault circuit interrupter receptacle
  2. A receptacle protected by a listed outlet branch circuit type arc-fault circuit interrupter type receptacle
  3. A receptacle protected by a listed combination type arc-fault circuit interrupter type circuit breaker This requirement becomes effective January 1, 2014.
 