In a service garage there are four lifts.
They replaced one and asked me to wire it.
They are fed with 20a-240v single phase twist lock chord drops.
The lifts have a 240v motor @ 17a
The lift has a box installed on it. The chord plug goes thru a "high limit" switch then to the motor.
The motor is NOT thermally protected.
The circuits are on 20 amp two pole breakers.
I wired the new lift as the original and the others are wired, BUT I'm thinking it should have been on a 30 amp circuit and thermal overload heaters installed.
Which would be the correct wiring?
As is, or new 30 amp circuits with motor overload protection?
Thank you.