List,
Here's what I'm telling the other electricians is possible without performing a change-out of the existing feeder. Please tell me if you see a problem with this...
Existing 480/3 feeder is on a 110a breaker. Currently it goes directly into the primary of a 480/208 75kva transformer. The secondary feeds a 225 amp main in the first of 2 full panels. The load is 55amps per phase. (Only computers.)
I'm suggesting we replace the 225 amp main breaker with a 75 amp main. Pull the transformer and install a 30kva instead. This will allow us to put in a 6 space 480 volt panel on the primary side of the transformer. From it we need to put in a 3 pole 50 and 20 breakers to feed a computer room hvac unit and get it off of the computer room feeder which is getting close to overloaded.
Some folks here say we would violate a "nameplate rating" rule. I've asked which section in the code that could be found but still haven't gotten an answer. Others think this could cause tripped breaker problems in the future.
Any opinions out there?
Mike Reisen
All Air & Electric
Arlington, Texas
Mike Reisen
All Air & Electric
Arlington, Texas