replaced 240v Pool motor, how to GFCI it?

Status
Not open for further replies.

KelleyCook

New User
Location
SE Michigan
Occupation
electrical is my hobby, not my paying job
Hello experts, I've seen a few questions on pools lately, but I could not find mine.

An pool guy recently replaced an 9.4 amp 240V pool pump. the installer noted that the switch for the switch only cut power to one of the hot lines (aka it was only single pole), so I replaced that with a double pole switch. When I did that I noted that the system was connected via a pair of 14AWG THHN along with a ground to the main Square D QO panel with a 30 (!!) amp 2P breaker.

The 30A breaker was obviously wrong (and dangerous), so I planned on downgrading the breaker to 15 amps.

Now I also see in the 2020 NEC, that 680.21D says replacing a pump now requires upgrading it to GFCI protection.

I wholly agree with the safety aspect and would like to do this properly, but I am unclear on how would I do this with a pump that is hardwired 240V with no neutral.

Don't GFCI breakers require a neutral connection (the pigtail?) or are there 240V GFCI downstream devices available?
 
I am closing this thread, in accordance with the Forum rules. This Forum is intended to assist professional electricians, inspectors, engineers, and other members of the electrical industry in the performance of their job-related tasks. However, if you are not an electrician or an electrical contractor, then we are not permitted to help you perform your own electrical installation work.

If I have misjudged the situation, if for example this project is related to your work, then send me a Private Message. If you can show me that I am wrong, and that you are a licensed electrician (or at least a licensed apprentice), then I will reopen your post, and offer an apology for the delay and inconvenience.