marybeth

Member
When updating an old 3 wire 220 receptacle to a 4 wire, can the ground connection be supplied from another grounded circuit in a remodeled, properly grounded area of the home? I would like to run the ground out of a box that houses an exterior 20A GFI box.
 
Re: Replacing 3 wire 220 receptacle with 4 wire

You would need to replace the old 2-wire cable with a new 3-wire cable w/ground.
Why is the "Upgrade" necessary?

Dave
 
Re: Replacing 3 wire 220 receptacle with 4 wire

The dryer we want to connect has a 4 prong plug and the old receptacle is only 3, which to the best of my ignorance, would not comply to code.
 
Re: Replacing 3 wire 220 receptacle with 4 wire

Although you could change the 4-prong cord to a 3-prong one, it would be better and safer to install a new 4-prong receptacle (with its own ground wire) to accommodate the cord. I'm not sure about the legality of changing the cord; my code book is out in the truck.

As for tying into the ground wire of the 20A circuit, I suspect that's not legal. The whole idea of an electrical circuit is that it's a closed loop. That is, a circuit is designed for the devices on it. Tapping into some other circuit's ground defeats the whole idea of a circuit and turns your installation into more of a web. The problem with a web is that you really don't know what loads are on a given conductor, greatly increasing the likelihood of overload.

[ April 20, 2005, 11:05 PM: Message edited by: jeff43222 ]
 
Re: Replacing 3 wire 220 receptacle with 4 wire

Jeff, all dryers I have seen are adaptable to either a 3 or 4 wire cord. The NEC changed it's requirements for seperate ground & nuetrals in 1996. However the NEC does not require an existing circuit to be upgraded just because someone bought a new dryer after 1996. Both style cords are still sold and come with instructions as to how to connect them correctly on a new or old dryer. The difference being the need for the bonding strap or the need to remove it to comply to NEC requirments.
Nothing cheesy about it!
;)
Dave

Edited to say "All dryers I Have seen"!

[ April 21, 2005, 02:14 AM: Message edited by: davedottcom ]
 
Re: Replacing 3 wire 220 receptacle with 4 wire

Marybeth,

Just buy a three prong cord or use the one off of your old dryer. Make sure that you connect the ground strap to the neutral connection where the dryer pigtail terminates (that would be the silver screw in most applications). The directions that come with the new dryer should spell this out somewhat clearly. If you don't have the old dryer cord, then go to Home Depot, Lowe's or the local hardware store. They'll have them. BTW, your dryer is just as safe with a 3-wire as it would be with a 4-wire.

Goodluck
 
Re: Replacing 3 wire 220 receptacle with 4 wire

I have run across several dryers that have factory installed 4-wire cords. If this dryer came with a factory installed cord and does not include instructions for changing the cord it should not be changed. If the manufacture does not intend for this cord to be changed I?m sure they don?t provide the bonding jumper necessary when using a 3-wire cord.
 
Re: Replacing 3 wire 220 receptacle with 4 wire

You cannot use the equipment ground that is in the 20 amp circuit to ground a 30 amp circuit.
 
Re: Replacing 3 wire 220 receptacle with 4 wire

Thanks, everyone. I can procede from here with confidence! So appreciate your input....Mb
 