jeff43222
Senior Member
- Location
- Minneapolis, Minnesota
I looked at a job today where the HO was complaining about flickering and dimming lights when the laundry machines were turned on. Load-wise, the 100A service was more than adequate (measured about 15A on each leg), and the BCs weren't overloaded. I opened up the panelboard and saw significant corrosion on the #2 Al conductor connected to the MCB (no one put on any antioxidant). I had her start the dryer, and I saw a spark come from the corroded conductor and saw the lights dim. The lug on the breaker was tight.
My plan is to replace the conductors from the meter socket to the panel, probably with #4 Cu to avoid future corrosion. My concern is if there's a lot of corrosion inside the breaker lug. If it's bad, is it possible to replace just the main breaker, or does this call for a panel swap? Other than the main breaker, the panelboard looks OK. It's a Sq.D. QOC-20M.
My plan is to replace the conductors from the meter socket to the panel, probably with #4 Cu to avoid future corrosion. My concern is if there's a lot of corrosion inside the breaker lug. If it's bad, is it possible to replace just the main breaker, or does this call for a panel swap? Other than the main breaker, the panelboard looks OK. It's a Sq.D. QOC-20M.