malachi constant
Senior Member
- Location
- Minneapolis
We are replacing a 120/240V delta high leg service with a straight 208V/3P/4W service. The utility transformers, service conductors, main switchboard, and a few panels are scheduled to be replaced. A few other switchboards and panels are scheduled to remain. What concerns do I need to have regarding existing loads and equipment?
My questions:
* Some of our 3-phase motor nameplates say 208-230, and some only say 230. Do we need to be concerned about the "230V only" equipment? We have pumps, an elevator, RTUs, compressors, lifts. (For instance one compressor says it is rated at 230/460 at 60hz, and 208/415 at 50hz. What are the chances there are issues here?)
* We plan on intercepting the feeders to existing-to-remain 3-phase switchboards and extending to the new service with three equal phase wires plus neutral and ground. Is it possible (likely?) the switchboard is currently fed with different size conductors? Are there potential issues here?
* We are replacing a few of the three-phase breaker panels with new. I assume the 120V/1P loads get refed from the same, and 208V/1-pole loads get refed from 2-pole breakers. What about 2-pole loads that straddled the 120V and 208V phases - just put those on new 208V 2-pole breakers?
The utility originally said they would let us keep the delta high-leg, but last week changed their mind and said we had to replace it with a straight-up 208/3. If there are enough concerns with existing panels/equipment I will challenge their decision. (This is all being driven by needing to replace an aged service entrance switchboard.)
Thanks!
My questions:
* Some of our 3-phase motor nameplates say 208-230, and some only say 230. Do we need to be concerned about the "230V only" equipment? We have pumps, an elevator, RTUs, compressors, lifts. (For instance one compressor says it is rated at 230/460 at 60hz, and 208/415 at 50hz. What are the chances there are issues here?)
* We plan on intercepting the feeders to existing-to-remain 3-phase switchboards and extending to the new service with three equal phase wires plus neutral and ground. Is it possible (likely?) the switchboard is currently fed with different size conductors? Are there potential issues here?
* We are replacing a few of the three-phase breaker panels with new. I assume the 120V/1P loads get refed from the same, and 208V/1-pole loads get refed from 2-pole breakers. What about 2-pole loads that straddled the 120V and 208V phases - just put those on new 208V 2-pole breakers?
The utility originally said they would let us keep the delta high-leg, but last week changed their mind and said we had to replace it with a straight-up 208/3. If there are enough concerns with existing panels/equipment I will challenge their decision. (This is all being driven by needing to replace an aged service entrance switchboard.)
Thanks!